BYTE order in ModBus #275
Replies: 7 comments 19 replies
-
Hi, |
Beta Was this translation helpful? Give feedback.
-
Hi, |
Beta Was this translation helpful? Give feedback.
-
This specific byte order I have got with wago controller. It is incredibly think. |
Beta Was this translation helpful? Give feedback.
-
Hi,
I try to test with new code (I downloaded latest working version of code from git) but I can find that ne capability. Can you help me whera I can find it?
BR
Tomáš
Tomáš Pastrňák
…________________________________
Od: Umberto Nocelli ***@***.***>
Odesláno: středa 23. března 2022 21:02
Komu: frangoteam/FUXA
Kopie: TomasAdvance; Author
Předmět: Re: [frangoteam/FUXA] BYTE order in ModBus (Discussion #275)
I would appreciate it if you could do a test with the modbus/wago branch and the new type Float32MBE. so that I can understand that I am on the right way. I don't put changes in a release if we haven't tested them before.
—
Reply to this email directly, view it on GitHub, or unsubscribe.
You are receiving this because you authored the thread.Message ID: ***@***.***>
|
Beta Was this translation helpful? Give feedback.
-
You have to download and install the modbus/wago branch (not from master) and then you should be able to configure tag of type Float32MBE |
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
Hi, |
Beta Was this translation helpful? Give feedback.
-
Hi Frangoteam,
Are they some posibility to define byte order in ModBus TCP for int32?
Thnaks for your answer.
We are connected to WAGO PLC 750-891, and if I understand the wago correctly the byte order for int32 is BADC. Is it any possibility to define byte order in fuxa scada system for int32 variable on modbus tcp?
Tomas
Beta Was this translation helpful? Give feedback.